Hi,
Please see the attached system and confirm whether the justification is accurate.
I received the comment below as well.
“The fire stopping of all the pipe going through the Q-deck is fire stopped from the top but has been applied at the top of the wood bottom plate of the floor and not against the concrete.”
Hello,
Thank you for reaching out to the Hilti Fire Protection Design Team to assist you with your firestop engineering needs.
Based on the firestop custom detail (FCD) you received from one of our engineers, you would not be able to seal to the wood framing above the concrete over metal deck assembly. You will either need to reinstall per the provided FCD, or submit for a revision to allow the engineer to review any changes and update your custom detail.
Hilti is proud to announce the launch of our engineering website, the HILTI CONSTRUCTION PLATFORM (HCP). This platform will be the home for all of your Fire Protection Engineering needs, including Engineering Judgment requests. You can find more information on how to access this new platform here: https://www.hilti.com/ej (US) or https://www.hilti.ca/ej (Canada.)
If you have any questions, please reach out to our customer service team at 1-800-879-8000 (US) or 1-800-363-4458 (Canada) for assistance.
Thank you,
Zach Rezazadeh
Fire Protection Engineer