Firestopping between new slab and existing wall
We are doing a multi-storey heritage project where the existing brickwalls are preserved with new floor slabs. The floor slab requires 2hr fire separation. The engineer required a drain mat as bond breaker between the new concrete floor slab and existing brick wall (see image below). Is there a firestopping system suitable for this condition?
1 Reply
Posted by GHINA KABBARAalmost 2 years ago
Hi Carl,
Please find attached tested system for concrete floor to concrete wall joint application. Please ensure that all system’s requirements can be met. If you have any questions, please contact us on cafirestop@hilti.com.