HAS B 105- can be cut to 6 inch

Posted by Samantha Lavergne11 days ago
HAS B 105- can be cut to 6 inch

Hello Hilti team.
My name is Parth. My company has its own fabiraction shop. My question is can I cut the Hilti HAS-B 105 Galvanized anchors ?
I ordered 8" long acnhors and Site needs only 6" long.
So, can we cut these 8" long- galvanized anchors and make them 6" long?

Thanks for help.
Regards,
Parth Patel
Assistant Coordinator
Fortran Steel Contracting LTD.
1340 Coker Street, Greely, Ontario, K4P 1A1
Email: parth@fortransteel.com
Office: (613) .821. 4014 ext. 7002
Email- parth@fortransteel.com

ROD,HAS B

1 Reply
Posted by Charbel Morcos8 days ago
Hilti Verified

Hello Parth,

Thank you for reaching out.

Typically, engineers avoid cutting anchor rods for the following reasons:

  • The corrosion resistance properties of the anchor could be reduced.
  • Cutting would remove the length identification mark on the anchor.
  • The threads of the anchor could be damaged, making it more difficult to remove the nut and washer.
  • the mechanical properties of the anchor could be changed, resulting in reduced load capacity


If corrosion is a concern, the Corrosion Handbook may be of use as a reference in this scenario.

Ultimately the decision to cut threaded rods is outside the scope of Hilti's testing and is at the discretion of the Engineer of Record on the project.

cutting,rods,galvanized,corrosion