Posted by Lisa Craigabout 2 years ago
In alberta code requirements

Can you run Plastic pipe in a rated shaft? My understanding was that the plumbing code said no. See attached photo. They have not built this shaft correctly and have reached out for some support

Shaft with multi penetrations,Plastic pipe

3 Replies
Posted by GHINA KABBARAabout 2 years ago
Hilti Verified

Hi Lisa,
Please send the details of the pipe including the size and material along with pictures for this case to cafirestop@hilti.com and we will get back to you as soon as possible.


Posted by  Mike Cunningtonabout 2 years ago

Building Code of Alberta will NOT permit combustible piping in a Vertical Shaft.


Posted by  Mike Cunningtonabout 2 years ago

Here is the excerpt from the New Alberta Building Code. However, this appears to be unchanged from the previous 2019 Alberta Building Code.

3) Combustible drain, waste and vent piping is permitted on one side of a vertical
fire separation, provided it is not located in a vertical shaft.