3 Replies
Posted by GHINA KABBARAabout 2 years ago
Hi Lisa,
Please send the details of the pipe including the size and material along with pictures for this case to cafirestop@hilti.com and we will get back to you as soon as possible.
Posted by Mike Cunningtonabout 2 years ago
Building Code of Alberta will NOT permit combustible piping in a Vertical Shaft.
Posted by Mike Cunningtonabout 2 years ago
Here is the excerpt from the New Alberta Building Code. However, this appears to be unchanged from the previous 2019 Alberta Building Code.
3) Combustible drain, waste and vent piping is permitted on one side of a vertical
fire separation, provided it is not located in a vertical shaft.